Actually the point of reading the pulses from the meter is that the meter is pretty damn close to being 100% accurate in real terms and is 100% accurate in terms of what you are paying for.
Absolutely, but I can still verify the data coming from the CT [*] by manually checking the meter periodically. If there's a big discrepancy I can adjust for it (and possibly buy the OptiSmart if I need to), although if the CT measurements aren't accurate then any hope of sub-metering with extra devices around the house goes out of the window. (Also, for this reason I wouldn't want to just have pulse counting at the main meter and use the CT to sub-meter (eg) my server, because if the CT would give inaccurate reading at the main meter then it'll still be giving inaccurate readings at my server but I won't know about it.)
To be honest the supplied CT in the kit isn't really suitable for measuring the consumption for a single device or a group of devices anyway, you need the IAM's for that.
The current transformer needs to be attached to a cable carrying a single pole (Live) of a single phase...If you attach it to say a mains flex feeding a 4 way extension bar then the two poles (Live and Neutral) of a single phase in the flex have opposing fields and therefore cancel each other out.